Jan 28th, 2008 at 12:14pm
Adjusting power in telnet will only briefly adjust power on the modem as the NMS UCP config will bring you back down to the configured nominal C/N for your network.
Dependent on the iDS, the Uplink Control Parameters (UCP) for a specific beam is set at the inroute level. (Older iDS's 6.x and below are set at the network level).
When the beam is commissioned the HNO will determine TDMA Nominal C/N for the upstreams and that is considered the "sweet spot" UCP for the beam/network. After setting the Nominal C/N he sets the fine and course adjusts. Normally Fine is set to one dB either side of the sweet spot and course adjusts are 3dB on either side of the 1dB fine adjusts. It will look like this.
| -3dB -|1dB| 9dB C/N |1dB| 3dB |
So, dependent on where your burst arrives, you may or may not get a power adjustment. If you do not, then you are meeting the UCP. If your modem is being told to pull power then you are arriving too hot. If you are being told to push power, you are arriving too low. The params above can be heavily skewed if you have different C/Ns (from multiple modems) arriving at the hub. That is why it is extremely important to ensure all VSATs operating in the beam are commissioned correctly and their Tx values are set to arrive within the UCP.
A lot of operators use a common set of inital and max power values for commissioning and they forget to follow up after node acquistion (and take a clear sky bseline) and revisit the configured params. Using "common" parameters is dangerous, as variopus nodes sit in different EIRP contour lines.
|